The sequence of operations for the pump system is as follows:\

  1. KM1 is energized to engage the electromagnetic coil, and pump 1 starts running in variable frequency mode.\
  2. When the working frequency of pump 1 reaches the upper limit of 48Hz, KM2 is energized to engage the electromagnetic coil. Pump 1 switches to operate in mains frequency mode. Then, KM3 is energized to engage the electromagnetic coil, connecting the variable frequency drive (VFD) to pump 2 for soft starting. Pump 1 continues to operate in mains frequency mode while pump 2 operates in variable frequency mode.\
  3. When the working frequency of pump 2 decreases to the lower limit of 15Hz, KM2 is de-energized, and pump 1 stops running. At this point, pump 2 continues to operate in variable frequency mode as a standalone pump.\
  4. When the working frequency of pump 2 reaches the upper limit of 48Hz, KM4 is energized to engage the electromagnetic coil. Pump 2 switches to operate in mains frequency mode. Then, KM5 is energized to engage the electromagnetic coil, connecting the VFD to pump 3 for soft starting. Pump 2 continues to operate in mains frequency mode while pump 3 operates in variable frequency mode.\
  5. When the working frequency of pump 3 decreases to the lower limit of 15Hz, KM4 is de-energized, and pump 2 stops running. At this point, pump 3 continues to operate in variable frequency mode as a standalone pump.\
  6. When the working frequency of pump 3 reaches the upper limit of 48Hz, KM6 is energized to engage the electromagnetic coil. Pump 3 switches to operate in mains frequency mode. Then, KM1 is energized to engage the electromagnetic coil, connecting the VFD to pump 1 for soft starting. Pump 3 continues to operate in mains frequency mode while pump 1 operates in variable frequency mode.\
  7. When the working frequency of pump 1 decreases to the lower limit of 15Hz, KM6 is de-energized, and pump 3 stops running. At this point, pump 1 continues to operate in variable frequency mode as a standalone pump. This cycle continues.\
  8. During the operation in mains frequency mode, the motor overload is protected by a thermal relay, and there is an alarm indication.\
  9. Each pump's VFD and mains frequency contactor must have electrical interlocks and mechanical interlocks externally.\
  10. The switching process involves the following steps: First, the MRS (Manual Reset Switch) is closed, stopping the output of the VFD with a delay of 0.2s. Then, the VFD contactor is opened with a delay of 0.5s, and the mains frequency contactor is closed. After that, there is a delay to close the next VFD contactor and disconnect the MRS contact, allowing the switching between VFD and mains frequency. \
  11. The switching between VFD and mains frequency is controlled by the temperature of the cooling water or the upper and lower limit switching frequencies of the VFD.